REVscene - Vancouver Automotive Forum


Welcome to the REVscene Automotive Forum forums.

Registration is Free!You are currently viewing our boards as a guest which gives you limited access to view most discussions and access our other features. By joining our free community you will have access to post topics, communicate privately with other members (PM), respond to polls, upload content and access many other special features. Registration is fast, simple and absolutely free so please, join our community today! The banners on the left side and below do not show for registered users!

If you have any problems with the registration process or your account login, please contact contact us.


Go Back   REVscene Automotive Forum > Vancouver LifeStyles (VLS) > House and Home Renovations

House and Home Renovations THIS SPACE OPEN FOR ADVERTISEMENT. YOU SHOULD BE ADVERTISING HERE!
Designing your new condo or townhouse? Renovating your kitchen? Share your photos and project ideas with other experts here! We're not just modifying our cars anymore..

Reply
 
Thread Tools
Old 10-25-2022, 05:12 PM   #1
Ready to be Man handled by RS!
 
StaceyQ's Avatar
 
Join Date: Mar 2004
Location: van
Posts: 81
Thanked 492 Times in 28 Posts
No/limited heating. Pictures included!

Hey guys,

I have in-floor heating and noticed that it never really heats up completely. I checked the zone valves and they all seem to be working.

I touched the piping coming out of the boiler and noticed it was hot until it reaches a t-junction where it seems to run into the return line.

Going up from that t-junction, the warm water (marked by yellow) goes into each zone.

My question is if the hot water should be in a t-junction going into the cold water? It seems to defeat the purpose and that is where the water starts going from HOT to warm leading to only warm water getting into the zone.

Please let me know if it's normal and if/how I could fix it.

Advertisement
StaceyQ is offline   Reply With Quote
Old 10-25-2022, 05:31 PM   #2
in the butt
 
donk.'s Avatar
 
Join Date: Aug 2016
Posts: 2,629
Thanked 3,222 Times in 1,184 Posts
Tap the recirc pump with your hand to make sure it's not hot (burn), then put your hand on it, it should be vibrating, during a heat call to at least one of the zones.

There should be an arrow on the red body of the volute assembly (back of pump), make sure this is pointing up

Pipe temperature on the discharge of the pump, and coming out of the boiler, should be similar, assuming the pump is on

Depending on how the thermostat is set up, it may very well be set up for an outdoor reset system.
Colder day = hotter supply
Summer day = probably 0 output
In other words, you will never feel hot piping, unless it's -10C outside.
Above is an assumption

Edit: what is the pressure of the system? Gauge on bottom left of boiler
Are there any heating zones above the height of the boiler? (2nd / 3rd floors)
__________________
Quote:
Originally Posted by Mr.Money
i hate people who sound like they smoke meth then pretend like they matter.

Originally Posted by ilovebacon
Does anyone have a pair of 25 pounds one-inch hole for sale at a reasonable price?


Originally Posted by Badhobz
I saw some bimbo live streaming her coffee order while standing in line. I wanted to slap the phone out of her hand and throw her into the bean grinder

Last edited by donk.; 10-25-2022 at 05:52 PM.
donk. is offline   Reply With Quote
Old 10-25-2022, 07:21 PM   #3
I contribute to threads in the offtopic forum
 
SSM_DC5's Avatar
 
Join Date: Sep 2004
Location: Canada
Posts: 2,758
Thanked 1,192 Times in 481 Posts
Quote:
Originally Posted by donk. View Post
...
Are there any heating zones above the height of the boiler? (2nd / 3rd floors)
What if the answer to this is yes?

I have some cold zones that feel the same temp as outside and the questionable zones are 2nd and 3rd.
SSM_DC5 is offline   Reply With Quote
Old 10-25-2022, 08:03 PM   #4
in the butt
 
donk.'s Avatar
 
Join Date: Aug 2016
Posts: 2,629
Thanked 3,222 Times in 1,184 Posts
@SSM

If the answer is yes, and the pressure in the system is less than 1psi per 2.31ft, then it's a problem

Ex, 2 story house, height of second floor, in floor heating is 11ft.
11ft / 2.31 = you need 5psi minimum.
Or 21ft (3rd floor), 21 / 2.31 = 10psi minimum.
Assuming the gauge is not faulty

Furthermore, you may have air vents that are airlocked, these need to be bled out. (Same as your car radiator loop, highest points may get airlocked)
Manual air vent = open till there's no air, if your unlucky, the gasket is gone and it will not re seal
Auto air vent = probably failed, or the 1/4cap has been tightened, loosen 1 turn, wait till it stops hissing, close back up

Or you have a couple of rats that made it into your closed loop heating system
__________________
Quote:
Originally Posted by Mr.Money
i hate people who sound like they smoke meth then pretend like they matter.

Originally Posted by ilovebacon
Does anyone have a pair of 25 pounds one-inch hole for sale at a reasonable price?


Originally Posted by Badhobz
I saw some bimbo live streaming her coffee order while standing in line. I wanted to slap the phone out of her hand and throw her into the bean grinder
donk. is offline   Reply With Quote
Old 10-25-2022, 08:12 PM   #5
Ready to be Man handled by RS!
 
StaceyQ's Avatar
 
Join Date: Mar 2004
Location: van
Posts: 81
Thanked 492 Times in 28 Posts
Quote:
Originally Posted by donk. View Post
Tap the recirc pump with your hand to make sure it's not hot (burn), then put your hand on it, it should be vibrating, during a heat call to at least one of the zones.

There should be an arrow on the red body of the volute assembly (back of pump), make sure this is pointing up

Pipe temperature on the discharge of the pump, and coming out of the boiler, should be similar, assuming the pump is on

Depending on how the thermostat is set up, it may very well be set up for an outdoor reset system.
Colder day = hotter supply
Summer day = probably 0 output
In other words, you will never feel hot piping, unless it's -10C outside.
Above is an assumption

Edit: what is the pressure of the system? Gauge on bottom left of boiler
Are there any heating zones above the height of the boiler? (2nd / 3rd floors)
The arrow is pointing up.

I have the thermostats in the houses cranked and the zone control manual overrides are loose (which I assume means they are working and hitting the end switch to call for heat?) and there's no noise or hum out of the pump. The pump itself is warm and I have tested that there is power going to it. The pump itself is warm, not hot. Can't tell if it's supposed to hum or whirr.

The pipe is cool/warm at/from the t-junction, past the pump, and into the zones. Is it normal to have the hot water run into a T and mix with the cold/return?

The upstairs is definitely cooler than downstairs. Maybe the pump is on its last legs?

Pressure is about 18PSI (picture attached).


Last edited by StaceyQ; 10-25-2022 at 08:24 PM.
StaceyQ is offline   Reply With Quote
Old 10-25-2022, 08:33 PM   #6
in the butt
 
donk.'s Avatar
 
Join Date: Aug 2016
Posts: 2,629
Thanked 3,222 Times in 1,184 Posts
@Stacey

The pump should have a minor vibration to it, hard to tell unless you handle them regularly.

If the power matches the nameplate rating, (leg to leg, not to ground) I would suspect the motor is seized, the impeller has disintegrated, the impeller is stuck to the volute.

Depending on your level of DIY, you can turn off the pump, close the supply valve to the pump, plus all zones. Then loosen the 4 Allen key bolts holding motor to the volute. Wiggle the motor off, drain the pressure until it stops, then fully remove it.
At this point you can turn the power on to the motor only, and verify if it actually spins.

Ps, the gauge is faulty, I doubt the heating temp is 260F. It may be possible that the 18psi is actually xpsi
Furthermore, just because there is pressure, does not mean there is flow

I could be wrong on all of the above, this is just what I see based by information provided over the eeeenternets

At this point, I would personally recommend you call out a professional, Incase things don't reseal, or leak, or you need to further diagnose.
4hrs labour, bill should be sub 500$ for a repair assuming no parts need replacing
__________________
Quote:
Originally Posted by Mr.Money
i hate people who sound like they smoke meth then pretend like they matter.

Originally Posted by ilovebacon
Does anyone have a pair of 25 pounds one-inch hole for sale at a reasonable price?


Originally Posted by Badhobz
I saw some bimbo live streaming her coffee order while standing in line. I wanted to slap the phone out of her hand and throw her into the bean grinder
donk. is offline   Reply With Quote
Old 10-25-2022, 08:39 PM   #7
Ready to be Man handled by RS!
 
StaceyQ's Avatar
 
Join Date: Mar 2004
Location: van
Posts: 81
Thanked 492 Times in 28 Posts
I may try to remove the pump and see how it goes.

I guess I'll have to refill the close loop system? Or does it auto refill?
StaceyQ is offline   Reply With Quote
Old 10-25-2022, 08:42 PM   #8
in the butt
 
donk.'s Avatar
 
Join Date: Aug 2016
Posts: 2,629
Thanked 3,222 Times in 1,184 Posts
The rusted PRV on the top left of the green expansion tank will auto fill the system.

You may, need to bleed air out of the system after doing the pump in/out. Unless there is an air bleed ontop of the actuator manifold. (Picture is cut off)
__________________
Quote:
Originally Posted by Mr.Money
i hate people who sound like they smoke meth then pretend like they matter.

Originally Posted by ilovebacon
Does anyone have a pair of 25 pounds one-inch hole for sale at a reasonable price?


Originally Posted by Badhobz
I saw some bimbo live streaming her coffee order while standing in line. I wanted to slap the phone out of her hand and throw her into the bean grinder
donk. is offline   Reply With Quote
Old 10-26-2022, 08:27 AM   #9
I contribute to threads in the offtopic forum
 
SSM_DC5's Avatar
 
Join Date: Sep 2004
Location: Canada
Posts: 2,758
Thanked 1,192 Times in 481 Posts
These are my auto air vents, the one at the back has no tiny cap on it.


getting 15 or 16 psi


I haven't seen any where I can manually vent from on the upper floors.

And here's a pic of the whole system incase it helps



Last edited by SSM_DC5; 10-26-2022 at 09:27 PM.
SSM_DC5 is offline   Reply With Quote
Old 10-26-2022, 09:34 PM   #10
I Will not Admit my Addiction to RS
 
Join Date: Apr 2001
Posts: 593
Thanked 913 Times in 158 Posts
1) First things first, determine if there is circulation of water in the zones. If the zone valve is open the water should go through that loop and come by via the return, which should also be warm/hot. If there is no circulation it would mainly be the circulator (pump) and/or air lock (more common on the upper floors). Try bleeding/flushing each loop to get rid of the air.
2) Won't be the outdoor reset because a) this older navien combi boiler didn't have outdoor reset and b) outdoor reset doesn't stop making hot water for hydronic heating. The whole point of the outdoor reset is that it changes the heating curve (for example if it was -10c outside, it would produce water at 140f for in-floor heating. If it was 10c outside, it would probably make it at 100f to save energy)
3) I'm not sure if that Honeywell circulator (pump) has it, put the Grundfos circulators has a removable cover on the housing that cover the shaft. You can remove it and see if the shaft is spinning without disassembling the circulator (be careful since these are wet rotor circulator meaning some water will leak out). FYI chances are if the circulator is seized and not spinning, the housing of the circulator would be too hot to touch.
4) That "T-junction" that you're asking about is "correct". It's one of the ways to pipe these high-efficiency boilers with multiple circulators for hydraulic separation. I say "correct" because it's technically not configured correctly, but still kind of does the job.
5) These older Navien combi boilers do not produce output for both domestic hot water usage and space heating at the same time. The 3-way valve prevents that and will prioritize domestic hot water production, meaning if someone is using domestic hot water, it will not make hot water for space heating.
6) Should really call a heating tech. Good luck getting one to show up right now since everyone turned their heating system on for the first time this week and found out it does not.
__________________
HKS | DAIZEN | TRD | TOM'S | K&N | B&M | FIGS | SSR
HKS PWR is offline   Reply With Quote
Old 11-20-2022, 05:26 AM   #11
Ready to be Man handled by RS!
 
StaceyQ's Avatar
 
Join Date: Mar 2004
Location: van
Posts: 81
Thanked 492 Times in 28 Posts
Update!

Boiler was messed up in various ways (leaking, wiring...etc). Navien replaced it underwarranty (phew!) but it still cost around $3.8k to get the system installed and piping fixed/other misc things. HKS PWR was pretty much spot on in his diagnosis. I used Coppersmith plumbing (run by a guy named Jackson). Dude's legit and honest.

But more importantly, here are the pictures.


Last edited by StaceyQ; 11-20-2022 at 05:33 AM.
StaceyQ is offline   Reply With Quote
This post thanked by:
Old 11-20-2022, 09:24 AM   #12
Waxin’ Punks
 
punkwax's Avatar
 
Join Date: Jun 2006
Location: South Surrey
Posts: 7,128
Thanked 6,044 Times in 2,077 Posts
+1 for Jackson.

Reminds me he has a little job left to do at my place as well.. obviously nothing urgently needed but thanks for the reminder nevertheless.
__________________
If you drive like an asshole, you probably are one.

Quote:
Originally Posted by MG1 View Post
punkwax, I don't care what your friends say about you, you are gold!
Quote:
Originally Posted by mikemhg View Post
What do your farts sound like then?
punkwax is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are Off



All times are GMT -8. The time now is 03:59 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
SEO by vBSEO ©2011, Crawlability, Inc.
Revscene.net cannot be held accountable for the actions of its members nor does the opinions of the members represent that of Revscene.net