Wiring, 230v extension chord
I want to make a 230v extension chord for my welder that runs off my dryer circuit. My welder draws 25A @ 230v at full load, max duty cycle 30%. I don't plan on welding anything on that high of setting, maybe 50% load.
I have a 50 ft 12/3 chord and a dryer plug.
Will this work?
__________________
┐(´—`)┌
|
|
|
03-04-2012, 09:09 AM
|
#2
|
|
I WANT MY 10 YEARS BACK FROM RS.net!
Join Date: Jan 2006
Location: Abbotstan
Posts: 20,721
Thanked 12,136 Times in 3,361 Posts
Failed 1,848 Times in 413 Posts
|
Chart here: Extension cord - Wikipedia, the free encyclopedia
12/3 should be fine for 50', although I wouldn't go any further than that.
__________________
Quote:
Originally Posted by Godzira
Does anyone know how many to a signature?
|
..
Quote:
Originally Posted by Brianrietta
Not a sebberry post goes by where I don't frown and think to myself "so..?"
|
|
|
|
03-04-2012, 10:29 PM
|
#3
|
|
I don't get it
Join Date: Feb 2002
Location: Coquitlam
Posts: 406
Thanked 30 Times in 20 Posts
Failed 27 Times in 6 Posts
|
its not smart, the welder draws more at full power then the wire is rated for.
im sure you'll be fine. its intermittent and you'll keep it on a lower setting then full load.
|
|
|
03-07-2012, 05:04 AM
|
#4
|
|
Proud to be called a RS Regular!
Join Date: Jun 2005
Location: 604
Posts: 133
Thanked 0 Times in 0 Posts
Failed 0 Times in 0 Posts
|
12/3 is not going to work, you'll just burn the wires cause it not rated for that kind of amperage. you must you 10/3 to make it work safely.
|
|
|
03-07-2012, 06:10 PM
|
#5
|
|
I told him no, what y'all do?
Join Date: Aug 2006
Location: Vancouver
Posts: 10,898
Thanked 6,625 Times in 2,929 Posts
Failed 110 Times in 72 Posts
|
i believe table 2 in the canadian electrical code shows for copper that #12 is rated up to 20 amps and #10 is rated up to 30 amps.
i think think you'd need #10 as pocha stated to be safe.
__________________
Feedback
http://www.revscene.net/forums/showthread.php?t=611711
Quote:
Greenstoner
1 rat shit ruins the whole congee
originalhypa
You cannot live the life of a whore and expect a monument to your chastity
|
Quote:
[22-12, 08:51]mellomandidnt think and went in straight..scrapped like a bitch
[17-09, 12:07]FastAnna glowjob
[17-09, 12:08]FastAnna I like dat
|
|
|
|
 |
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
All times are GMT -8. The time now is 01:20 AM.
|